Brand new craftsman air compressor trips breaker instantly
#1
Registered User
Thread Starter
Join Date: Aug 2005
Location: Lafayette IN
Posts: 228
Likes: 0
Received 0 Likes
on
0 Posts
Brand new craftsman air compressor trips breaker instantly
I just got a new craftsman air compressor and im having problems with it. When I first plugged it in, it did nothing, and I mean nothing. After switching it on and off a few times I got a quick click and im intantly standing in complete darkness. After feeling my way to the breaker box (in garage) i reset the breaker, try it and it trips again. I reset and turn the compressor by hand to be sure it feels ok. All is good and spun freely. I try it again and it starts. I let if fill up and kick off. I hook up an air sander to drain some air and make it kick back on. It gets down to about 90 psi and still nothing, no clicks, just silence. Its supposed to cut in at 120 and out at 150. so Im standing there scratching my head on why it didnt kick on and then I hear a click and then darkness again.
long story short , sometimes it starts... sometimes it doesnt. Once its running it works great. but it only starts about 20% of the time.
Also, its not like it jammed up or binding or anything like that. Like I said, just a quick click and then trips the breaker. I have a 20amp breaker in my garage. The only other thing on in the garage were two 75w light bulbs in the ceiling and a 45w bulb in the garage door opener. I tried with all these lights off and got the same results. I also took it in the laundry room (30 amp) and got the same results.
Anybody know what to look for first or should I just take it back? Im not sure if they have more. I hope they do because I was planning some body work on the 4Runner this weekend
long story short , sometimes it starts... sometimes it doesnt. Once its running it works great. but it only starts about 20% of the time.
Also, its not like it jammed up or binding or anything like that. Like I said, just a quick click and then trips the breaker. I have a 20amp breaker in my garage. The only other thing on in the garage were two 75w light bulbs in the ceiling and a 45w bulb in the garage door opener. I tried with all these lights off and got the same results. I also took it in the laundry room (30 amp) and got the same results.
Anybody know what to look for first or should I just take it back? Im not sure if they have more. I hope they do because I was planning some body work on the 4Runner this weekend
#3
its not the compressor. Its your wiring.
We had the EXACT same "issue" with a craftsman compressor (the black tank one) at work. Problem was the voltage drop between the breaker box and the outlets. The wiring was not large enough, and the current strong enough to handle the current draw used by the compressor.
You need to get an electrician out there to remedy that problem, or you will continue to have the same issue.
trust me when i say there is NOTHING wrong with the compressor.
We had the EXACT same "issue" with a craftsman compressor (the black tank one) at work. Problem was the voltage drop between the breaker box and the outlets. The wiring was not large enough, and the current strong enough to handle the current draw used by the compressor.
You need to get an electrician out there to remedy that problem, or you will continue to have the same issue.
trust me when i say there is NOTHING wrong with the compressor.
#5
Registered User
Thread Starter
Join Date: Aug 2005
Location: Lafayette IN
Posts: 228
Likes: 0
Received 0 Likes
on
0 Posts
hmm. thats not what I want to hear considering I rent this place. Its a duplex and I doubt they would do it for me.
Im not telling you your wrong, but what about the compressor not even doing anything in the beginning. It didnt even click or trip the breaker. It was like it wasnt even plugged in. The first 15-20 times I turned it on it did nothing.
Also, is it common to have this wiring problem in homes? These places are only about 4 years old. The outlet I was using is only about 7 inches from the main box.
Im not telling you your wrong, but what about the compressor not even doing anything in the beginning. It didnt even click or trip the breaker. It was like it wasnt even plugged in. The first 15-20 times I turned it on it did nothing.
Also, is it common to have this wiring problem in homes? These places are only about 4 years old. The outlet I was using is only about 7 inches from the main box.
#7
Registered User
Thread Starter
Join Date: Aug 2005
Location: Lafayette IN
Posts: 228
Likes: 0
Received 0 Likes
on
0 Posts
well it says 15 amp on the website. Here are the specs
http://www.sears.com/shc/s/p_10153_1...+%26+Inflators
http://www.sears.com/shc/s/p_10153_1...+%26+Inflators
Trending Topics
#8
Registered User
How many amps is the breaker rated for that is on the circuit that you are using for the air compressor? Try plugging it in to a circuit with a breaker that is rated at more than 20 amps. The air compressor should be the only thing on the circuit.
I kind of remember hearing somewhere that a breaker blows at 70% or 80% of its rated amperage or something like that. 15 amps would be right at the limit if that is true.
I kind of remember hearing somewhere that a breaker blows at 70% or 80% of its rated amperage or something like that. 15 amps would be right at the limit if that is true.
#9
I have the same compressor but a different brand. The only time I haven't been able to get it to fire up is when I am using an extension cord that is too small of a guge & there is too much of an amperage drop. The fix was to upgrade the cord. If you are plugging into a 20amp circut 7 feet away from the box, you should have no problem at all. You should take it back to the store.
#10
Registered User
Join Date: Jan 2007
Location: Middleburg, FL
Posts: 614
Likes: 0
Received 0 Likes
on
0 Posts
I have had 2 of the Craftsman compressors very similar to that, and never had any issues (other than losing my hearing) wherever I use them.
I, too, think the compressor is at fault.
I, too, think the compressor is at fault.
#11
Registered User
Thread Starter
Join Date: Aug 2005
Location: Lafayette IN
Posts: 228
Likes: 0
Received 0 Likes
on
0 Posts
Today after work a buddy and I took the compressor over to his house and tried it. It worked perfectly fine. He has a 15 amp circuit on the outlet we used. I cycled it about ten times and didnt have a single problem, not even a hint of trouble.
I brought it back to my house and tried it again and it still tripped the 20amp breaker instantly. The only other oulet in the garage is the one in ceiling for the garage door opener. We put the compressor up on the gate of my runner so the cord would reach up there and it worked fine. I started it up about 5 or 6 times. The confusing part is that the cieling outlet is on the same breaker as the one I was having problems with. When plugged into the cieling outlet It even started with my lights on and refridgerator plugged. I did see a slight dim of the lights upon initial start but that is normal.
I dont think an extention cord would be good to run all the way from the ceiling and down the wall. Would probly have to be about 25' of cord.
So I have narrowed it down to that single outlet that has the problem. Im not comfortable with messing with electricity so I guess im going to try to find somebody I know or a friend who knows what to do next.
I brought it back to my house and tried it again and it still tripped the 20amp breaker instantly. The only other oulet in the garage is the one in ceiling for the garage door opener. We put the compressor up on the gate of my runner so the cord would reach up there and it worked fine. I started it up about 5 or 6 times. The confusing part is that the cieling outlet is on the same breaker as the one I was having problems with. When plugged into the cieling outlet It even started with my lights on and refridgerator plugged. I did see a slight dim of the lights upon initial start but that is normal.
I dont think an extention cord would be good to run all the way from the ceiling and down the wall. Would probly have to be about 25' of cord.
So I have narrowed it down to that single outlet that has the problem. Im not comfortable with messing with electricity so I guess im going to try to find somebody I know or a friend who knows what to do next.
#12
Registered User
Join Date: Jan 2008
Location: Los Angeles
Posts: 230
Likes: 0
Received 0 Likes
on
0 Posts
Maybe its the outlet. Or maybe that specific breaker is bad or says 15 but isnt.
And although the compressor pulls 15amps running, it pulls more than that at first, the surge amp draw.
And although the compressor pulls 15amps running, it pulls more than that at first, the surge amp draw.
#13
Contributing Member
Join Date: Feb 2004
Location: Appleton, Wi. USA
Posts: 903
Likes: 0
Received 0 Likes
on
0 Posts
A few probable causes. #1 Out go the lights, Typically rental units are wired as cheaply as possible (this doesn't make it a bad wiring job, just cheap). What this means is no dedicated circuits other than what's required. Also I would be willing to bet there are other things on that circuit, possibly bathroom GFCI's. #2 The receptacle may be installed the quick and easy ( it may be back stabbed rather than on the termination screws) not the most solid connection for items with a large in rush current. The label may say 15 amp circuit ( usually running current) but the start up ( in rush) may be 20). Circuit breakers are normally designed to run at 80 percent load ( a 15 amp is really good for 12 amps and a 20 is good for 16 amps) a good breaker will only work at the full rating for short term. #3 possible bad terminations at the panel (grounded and grounding connections the green or bare copper and the white or gray also the breaker connection) Since the lights go out any splice or connection along the way could be loose (lights, receptacles, switches) #4 Is the receptacle a GFCI (has the reset/test buttons) or the breaker a GFCI ( has the yellow test button) both not ideal for motor loads. Good luck, I'd come over and check it out but your a bit of a drive away.
#14
Daly
I just got a new craftsman air compressor and im having problems with it. When I first plugged it in, it did nothing, and I mean nothing. After switching it on and off a few times I got a quick click and im intantly standing in complete darkness. After feeling my way to the breaker box (in garage) i reset the breaker, try it and it trips again. I reset and turn the compressor by hand to be sure it feels ok. All is good and spun freely. I try it again and it starts. I let if fill up and kick off. I hook up an air sander to drain some air and make it kick back on. It gets down to about 90 psi and still nothing, no clicks, just silence. Its supposed to cut in at 120 and out at 150. so Im standing there scratching my head on why it didnt kick on and then I hear a click and then darkness again.
long story short , sometimes it starts... sometimes it doesnt. Once its running it works great. but it only starts about 20% of the time.
Also, its not like it jammed up or binding or anything like that. Like I said, just a quick click and then trips the breaker. I have a 20amp breaker in my garage. The only other thing on in the garage were two 75w light bulbs in the ceiling and a 45w bulb in the garage door opener. I tried with all these lights off and got the same results. I also took it in the laundry room (30 amp) and got the same results.
Anybody know what to look for first or should I just take it back? Im not sure if they have more. I hope they do because I was planning some body work on the 4Runner this weekend
long story short , sometimes it starts... sometimes it doesnt. Once its running it works great. but it only starts about 20% of the time.
Also, its not like it jammed up or binding or anything like that. Like I said, just a quick click and then trips the breaker. I have a 20amp breaker in my garage. The only other thing on in the garage were two 75w light bulbs in the ceiling and a 45w bulb in the garage door opener. I tried with all these lights off and got the same results. I also took it in the laundry room (30 amp) and got the same results.
Anybody know what to look for first or should I just take it back? Im not sure if they have more. I hope they do because I was planning some body work on the 4Runner this weekend
The following users liked this post:
2ToyGuy (11-26-2021)
#16
Registered User
Join Date: Mar 2015
Location: Nampa, Idaho
Posts: 159
Likes: 0
Received 0 Likes
on
0 Posts
Popping breakers, interesting theories here
Trying basic "troubleshooting" is the proper route, but with formally made in USA now made in China,
ya even Craftsman, you have more plausibility of cheap junk. (at a high price).
If it's rated @ 15A it should work fine, 110VAC assumed??
If it works at friends house, it's fine.
Circuit breakers are rated higher than listed, a 15 will pop at about 18 or so.
15 is a static rating, dynamic is a bit higher.
Depending on the type of OL, breakers react differently..
Direct shorts snap the breaker quickly (Ohm's Law) Direct short=MAX current.
Slow overloads fatigue the breaker over time (running close to max rating)
starts causing them to reset at less than rated amperage,
it's a problem in older residential units, it takes a long time,
it's obvious if you look at it..
Wire sizes aren't an issue unless an unlicensed or unethical goober/homeowner got in there, codes require specific values..
J
Nuclear Submarine Repair Electrician (Retired)
ya even Craftsman, you have more plausibility of cheap junk. (at a high price).
If it's rated @ 15A it should work fine, 110VAC assumed??
If it works at friends house, it's fine.
Circuit breakers are rated higher than listed, a 15 will pop at about 18 or so.
15 is a static rating, dynamic is a bit higher.
Depending on the type of OL, breakers react differently..
Direct shorts snap the breaker quickly (Ohm's Law) Direct short=MAX current.
Slow overloads fatigue the breaker over time (running close to max rating)
starts causing them to reset at less than rated amperage,
it's a problem in older residential units, it takes a long time,
it's obvious if you look at it..
Wire sizes aren't an issue unless an unlicensed or unethical goober/homeowner got in there, codes require specific values..
J
Nuclear Submarine Repair Electrician (Retired)
#17
Registered User
Join Date: Mar 2015
Location: Nampa, Idaho
Posts: 159
Likes: 0
Received 0 Likes
on
0 Posts
Thank God for Tesla, the inventor of AC
There is essentially no "voltage drop" in AC thanks to Tesla and Westinghouse, that would be the realm of Edison the liar and inventor of Concrete Furniture, amongst other stuff J just a wee bit of factual truth